Burnham: Flame Sensor problem or something else?
SBC
Member Posts: 1
I have a burnham series 2 gas boiler. When heat is called for, the pilot flame kicks on but the main burners will not. The unit clicks for about 30 sec then gives up. Service tech used a file to clean the sensor and it worked fine for several hours then started doing the same thing again. Tech said I needed to order a new pilot ignitor sensor assembly.
I don't think he checked for other possible problems. Is there something else I should check before spending $400 on getting a new assembly put in? Thanks.
I don't think he checked for other possible problems. Is there something else I should check before spending $400 on getting a new assembly put in? Thanks.
0
Comments
-
a file on a flame sensor YIKES
He should never have used a file on a flame sensor, steel wool is the weapon of choice. It sounds like you have a spark ignition and the sensor is permanatly mounted in the pilot assembly. Clean it again and the pilot assembly allaround it and see how that works.0 -
Try
grounding0 -
Try
You should try to get another tech over and have him check it out. I would not advocate that you try it yourself. Yes, there may be other issues, and a qualified tech should be able to diagnose your issue.0 -
It could be a bad
ignition control module (ICM); the pilot will often rectify properly, but one of the relays in the ICM may not close the circuit to power open the burner. Usually a Honeywell S 8610U 1003 universal replacement; there are also others.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements