Fin-Tube Baseboard
CMadatMe
Member Posts: 3,086
Does anyone have or know where I can find the formula that is used to calculate btu output for fin-tube baseboard. Baseboard charts give you the average ratings at 150, 160, 170, 180. None give you the 155, 165,175 average ratings.
Example. Suntemp 700 Series at a water temp of 170 degrees and a flow rate of 2gpm gives you 514 btus a foot and at a water temp of 160 degrees with the same flow rate 442 btu's per foot. What will it give me with a 165 degree water temp at the same flow rate of 2GPM?
look here
This is the Slantfin sheet
[url=http://www.slantfin.com/documents/285.pdf]http://www.slantfin.com/documents/285.pdf
To answer the example, I'd assume the response between those two temperatures is approximately linear and say 165F is about 478 BTU, plus or minus a couple....0
- 120 Geothermal
