antler/menorah pitch for main vents?
jpf321
Member Posts: 1,568
I just reviewed the drawing that has been posted in these forums before... <a href="http://www.heatinghelp.com/images/posts/983/resize_Multiple%20Venting.jpg">http://www.heatinghelp.com/images/posts/983/resize_Multiple%20Venting.jpg</a> ..
Is it ok that there is little to no pitch using an antler for main vents?
Should I figure out how to pitch it?
Will the steam and condensate excuse each other on 1/2" pipe?
Will water hammer be a problem without pitch?
How will I ensure that the antler drains?
thanks
Is it ok that there is little to no pitch using an antler for main vents?
Should I figure out how to pitch it?
Will the steam and condensate excuse each other on 1/2" pipe?
Will water hammer be a problem without pitch?
How will I ensure that the antler drains?
thanks
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
0
Comments
-
venting menorah size
i have only used 3/4'" pipe for vents, because i would think that the 1/2" could be a little small especially at the beginning of the cycle.
in your photo 27, where the small vents are, you could cut out the short verticals and put in a proper tee, for 3/4" pipe. do a search for "removing nipple" for the procedure.--nbc0 -
as long as you don't have reverse
pitch you should be okay..you just can't load up a half inch pipe with much tho..only 2 gorton #2 main vents on 1/2'' pipe.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
plan on tapping the main...
I plan on tapping the mains and leaving the small vents frozen in place. this is mainly b/c I think that section of pipe may often get stack on it. if it gets stacked, even if I raise my vents way up above DimA .. the opening will be flooded until my slow returns drain. those vents are only 14in above water line and while it is a domestic and the dead men, according to TLAOSH (pg 25.) may have used 14" .. I'd feel much better about going on top of the mains (the bottoms of which are 24" AWL)
I may attack that small vent area in order to attempt a wet return cleanout.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
nope not reversed...
and I only plan on 1pc #2 on the 1/2" antler. Thanks though, very valuable rule of thumb...btw, how many #2s can go on 3/4" pipe .. I see that steamhead has presumably 3pcs #2 on x/y" pipe.
I see that you note that open 1/2" pipe can vent 2.6CFM @ 1oz.
Question: Is it perhaps better to use 2pcs 45deg Ells with close nipple rather than a 90deg Ell to smooth the turn? Or perhaps to even bend the pipe rather than use Ells. Just wondering about in-pipe friction and turbulence..1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
four #2's and a single #1
equal a 3/4'' pipe..yes a smoother turn does place less ''backpressure'' or friction loss on the air, or steam for that matter.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
from your data table...
I see that now 4pcs #2 and a 1pcs #1 = 9.5CFM = 3/4" pipe @ 3OZ. Thanks!1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements