Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Service Tech

Steph
Member Posts: 2
I have a customer with a system 2000 oil fired hot water boiler. It has four zone valves 3 heating and 1 domestic hot water and the Energy Manager control is for 4-zones. They would like to add a 5th heating zone. Is there any way to piggy back this control for the additional zone or do we need to replace the complete control?
0
Comments
-
System 2000
I believe you would need to install the expanded digital manager. That’s available as a 10 zone or a 15 zone manager. So you could install the 10 zone manager.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements