Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
a very bad idea...
Timco
Member Posts: 3,040
No heat call, about 45 minutes south of me. I get there to find the place pretty warm, and a odd 'smell' in the air. Almost immediately I get a ache in the back of my head, and as I look into the kitchen I notice the gas range with all 4 burners on high and the gas oven on full blast, door open. I let the place air out and explain that is a great way to not wake up...it was that way all night. as for the no heat call, air bound coil on a hydro-air unit.
Tim
Tim
Just a guy running some pipes.
0
Comments
-
That stove
was way out of adjustment. You were smelling aldehydes, and ANY time you have aldehydes you have CO!
My own stove was the first thing I ever tested when I got my analyzer. It was over 1100 PPM CO/AF.
Get thee back to that house with your analyzer and test that puppy. I know what you're going to find!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
return trip
Fortunately, the manway gasket is dumping water and I have to schedule a return trip. I did not bring my analyzer because I knew this was a coil issue and have already tested the boiler. Good idea to adjust it but will explain it is still not a heat source....
TimJust a guy running some pipes.0 -
You can bet
they'll use the stove for heat again. Test it!
I once went to a neighbor's house for a reason I have forgotten. When she opened the door, the aldehyde smell hit me in the face. I had her shut the stove down and open the windows, got my analyzer and it was over 2500 PPM! Some adjustments took care of that.
Several years later, this was the house where I first met The Lovely Naoko.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements