Opinions on the Peerless Purefire? I'm scheduled to do a start up on two in the morning.
Purefire
Not a bad little boiler at all, I already have 25 of them in! Easy to program and install and very reasonably priced.0 -
Great boiler
Not much to a Purefire like JamieP said, they have made things very simple. Make sure the heat exchanger is at minimum level and preferably slightly tilted back, check gas pressures static and full fire. Preferably with other gas appliances in the building fired as well, you want to make sure you do not have excessive pressure drop not much more than 1" wc should be fine, check combustion, proper flow and piping arrangements etc etc.0