Intermitant fireing

JM_2
Member Posts: 108
I am having an intermittent firing issue with my Power pile Nat gas steam boiler. It has run fine since i bought the house 5 Yrs ago.
When i first got it, I had to replace a leaky pressure relief valve and lower the mechanical pressure troll to a differential of 1 with cut in at .5
It had been set higher.
All of a sudden the unit is occasionally not firing .
First I thought the pigtail may be clogged but its easy to blow though.
I notice however that if I actuate the pressure troll switch a few times it seems to fire. If I test the low water cut out the unit shuts down, but wont restart unless i activate the pressure troll switch a few times. I know the low water float is OK because I can hear it.
I replaced the pressure troll and everything was fine for about a week to ten days, then it got funky again. This time I called in the gas CO since I have a service plan, The tech poked around and noticed that when you activate the pressure troll switch a few time it would fire so he replaced the pressure troll again. So far so good, but I assume I will have the problem again soon. What are the odds that the new pressuretreioll that i installed was defective. I am guessing the the problem lies elswhere. Any ideas?
When i first got it, I had to replace a leaky pressure relief valve and lower the mechanical pressure troll to a differential of 1 with cut in at .5
It had been set higher.
All of a sudden the unit is occasionally not firing .
First I thought the pigtail may be clogged but its easy to blow though.
I notice however that if I actuate the pressure troll switch a few times it seems to fire. If I test the low water cut out the unit shuts down, but wont restart unless i activate the pressure troll switch a few times. I know the low water float is OK because I can hear it.
I replaced the pressure troll and everything was fine for about a week to ten days, then it got funky again. This time I called in the gas CO since I have a service plan, The tech poked around and noticed that when you activate the pressure troll switch a few time it would fire so he replaced the pressure troll again. So far so good, but I assume I will have the problem again soon. What are the odds that the new pressuretreioll that i installed was defective. I am guessing the the problem lies elswhere. Any ideas?
0
Comments
-
I had the same issue,,
a few years back. On mine it was the pilot generator,,, any screwed terminal connections must be clean & tight also any splices in the wiring should be soldered(as opposed to just twisted).
Had no-problems since. :-)0 -
The technician should check the generator...
for proper output both under load and without load. Powerpile generators last a long long time but do eventually fail. Also the gas valve may need to be checked too.
BoilerproThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 948 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements