Tridicators For Supply lines leaving boiler room?

jb_14
Member Posts: 13
I'm having a radiant hydronic system built. I want to be able to get good temperature and pressure info on all the zones in my boiler room so I can see delta t, relative zone performance, troubleshoot, etc.
What do you guys think of the dual temp/pressure gauges for the supplies and returns as they leave the boiler room/circulator mount wall ?
Also - How do I figure out what Tee to use (just a 3/4x3/4x1/2" brass sweat tee with 1/2" threaded branch?), and what thermo well and stem length for 3/4 supply and return pipes? Is the thermometer/well supposed to be down into the middle of the 3/4 pipe - 'in the flow'?
thanks for any thoughts.
boshart?
terice?
Boshart Tridicator?
<a href="http://randolphindustrialsupplies.com/Cat/BST/Tridicators.pdf">http://randolphindustrialsupplies.com/Cat/BST/Tridicators.pdf</a>
What do you guys think of the dual temp/pressure gauges for the supplies and returns as they leave the boiler room/circulator mount wall ?
Also - How do I figure out what Tee to use (just a 3/4x3/4x1/2" brass sweat tee with 1/2" threaded branch?), and what thermo well and stem length for 3/4 supply and return pipes? Is the thermometer/well supposed to be down into the middle of the 3/4 pipe - 'in the flow'?
thanks for any thoughts.
boshart?
terice?
Boshart Tridicator?
<a href="http://randolphindustrialsupplies.com/Cat/BST/Tridicators.pdf">http://randolphindustrialsupplies.com/Cat/BST/Tridicators.pdf</a>
0
Comments
-
Tridicators For Supply lines leaving boiler room,,
Boshart handles OK import stuff,, but you only get what you pay-for.
You must be Canadian(like me), so for more quality & accuracy I look to Winters . They are available through most supply-houses and have a good product.
I don`t use tridicators except at the boiler,, usually I`m concerned about the D/T temperature so I buy the Winters T174,,,http://www.winters.com/2008_PDF/TSW.pdf, with a 1/2" NPT well that is protruded into the main-flow at least half the diameter of that piping.
They are removable from the well(without draining),, quite accurate,,, and easy on the pocketbook.0 -
Plugs
I would use "Pete's" plugs , P/T plugs. Cheaper and more accurate. If you can, install a tee in place of an elbow and put the pete's plug on the run of the tee.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 948 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements