Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

boss

Options
woodtk
woodtk Member Posts: 1
I have 3 zones on my boiler system with a pump on each zone do I need to have a zone valve on those zones also or is the pumps all I need? Thanks

Comments

  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    Options
    No zone valves, but...

    If the circulators do not have a flow-check valve in them, you will need one in the supply line to each zone. If the piping is large, you may want a check valve in the return as well (it depends, as usual).



    N.B.: I am not a professional.
This discussion has been closed.