I have 3 zones on my boiler system with a pump on each zone do I need to have a zone valve on those zones also or is the pumps all I need? Thanks

Comments

  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666
    No zone valves, but...

    If the circulators do not have a flow-check valve in them, you will need one in the supply line to each zone. If the piping is large, you may want a check valve in the return as well (it depends, as usual).