main air vent
STEAM DOCTOR
STEAM DOCTOR Member Posts: 2,388
good afternoon. i have a 20' 2" main and a 1 1/2" main that is about 15' to the end plus another 15' as a dry return . which air vent should i be using. on the smaller main i only have access to the end of the dry return. thanks.
    Steamhead Member Posts: 17,843
    I'd use
    a Gorton #1 or Hoffman #75.
    What vent do you have on the other main?
    Consulting
  • STEAM DOCTOR
    no vent
    Thanks. i don't think there is a vent on the 1 1/2" main (basement is finished so hard to tell). the plan is to add a tee at the end of the dry return (the end of the main is not accessible). on the 2" main there is a Hoffman 45 which according to Hoffman's web site is not a main vent.
    You're right, it's not
    and you can vent that main with the same model vent.
    Consulting
  • STEAM DOCTOR
    edited October 2009
    thanks
    which is better the gorton 1 or the hoffman 75
    They're about the same
    but the 75 is typically more expensive. Also it's taller, which may be a factor if your height is limited.
    Consulting
  • STEAM DOCTOR
    gorton #2
    would the gorton#2 be beneficial or would it be overkill. thanksY
    On such a short main
    it would be more than needed.
    Consulting
  • STEAM DOCTOR
    thanks
    thanks for the info