OK to use clamp-on mechanical T to add main vent, instead of drilling and tapping?
Mike_K
Member Posts: 1
When adding a main vent to a 2" main, can I drill a hole and then use a mechanical T that screws or clamps onto the pipe, as opposed to tapping threads into the pipe? Are the gaskets on these mechanical Ts ok to use with steam?
0
Comments
-
If low pressure steam I would,,
drill the 2"(on the top of course), and tap the hole ½" and not think twice about-it,, your going to have to drill the hole anyway,,, but the BEST way is a welded-on thread-o-let,,,,,, and you already knew that. :-)
"Saddle-type" fittings can come back to haunt you.0 -
tapping for a vent
Unless you don't have the room for it, it is just as easy to cut the pipe, thread in a tee and a union and be done with it. Drilling a 1/2" hole and then tapping it with limited over head room can be a lot of work. And it can be very difficult to get the tap going straight. In most cases, with a hand held power threader, we can install a tee and union in 15-20 minutes tops.....not easy work either but a much better job.0 -
Gasket probably can't handle steam
I sell mechanical tees (along with a lot other hydronic products) and our max water temp is 230 deg F for our gaskets. If you are using steam then I very much doubt there is a gasket that can handle it.0 -
No.
I assume you're talking about a Victaulic- type fitting. I've been asking them for years and they say it's a no-go. They're not coming up with a suitable gasket in the foreseeable future.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
It ain't the gasket......
None of their fittings are rated for steam, and they have no plans to get them rated.0 -
It is the gasket
Sorry Rich I disagree. I work for Victaulic. You are partially correct, none of the fittings are rated for steam but that is because of the temperature limitation on the gasket. The gaskets only go to 230 deg F, in some cases 250 deg F. Steam is too hot for the gaskets. For that reason we have never bothered to put a steam rating on the fittings. JohnNY is correct in that we do not have a steam gasket or any plans to come out with one yet.0 -
Can't argue with you Peter,
I got my info from a rep who works for Vic. But 250 would be more than enough for most of our work. HINT,HINT.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements