Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Small Steam Radiator

Have a small bathroom served by a one pipe steam radiator, 17 x 25 x 3.5 and looks like a 3 row or tube.  Contractor wants to either recess this radiator into the wall or replace with what I believe is a convector to save space.  Good idea?  Bad idea?  I don't want problems where none currently exist and how do I know if this convector is sized correctly?  Thanks.

Comments

  • Steamhead
    Steamhead Member Posts: 17,312
    It's always a bad idea

    to replace a cast-iron radiator with a fin-tube unit if the rest of the system is cast-iron. The convector would cool down much faster when the boiler shuts down and the room will go cold.



    A slight recess would work, as long as there is 6 inches or so recessed above the radiator to allow warmed air to come off the top.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
This discussion has been closed.