expansion tank sizing

bill_105
Member Posts: 428
Is it possible to oversize an expansion tank? I had a brand new #60 tank charged to 12 lbs. and the relief valve leaked on two different boilers. After installing a, " By the book" tank, everything was fine. I'm thinking that diaphragm just did not want to move. Words of wisdom are greatly apprecitated
0
Comments
-
If you`re sure
about the acceptance volume it should have worked!
Complete system content is the key!0 -
Diaphragms DO stick...
I've had probably half a dozen of them in the stuck position, brand new, out of the box, from numerous and different maufacturers,
Unless your system is doing heating AND cooling, it is virtually impossible to oversize the expansion tank.
The ONLY thing lost in over sizing, is money...
To UN stick a sticky diaphragm, hook the tank up to city water pressure and exercise it a few times. THen when pressurizing the new system, keep the pressure of the tanks a few pounds higher than the required fill. This will keep the diaphragm off the face of the tank.
ME0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 948 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements