Leak in Underfloor Tubing?
PaulT
Member Posts: 1
I have a 10 year-old hydronic in-floor heating system. Lately I have noticed some moisture discoloration of my wood floor joints in an area in the kitchen which I believe may be coming from a small leak in the pex tubing in the slab. Is there a way to test whether the leak is coming from the hydronic system this without removing the wood floor and jackhammering the slab?
0
Comments
-
Is,,,
the system losing pressure?
Can you isolate the floor tubing from the rest of the system?0 -
Testing for leaks
PEX leaks in slab can be determined by isolating the radiant manifold and pressurizing to 50 or 60 PSI. If the gauge drops, there's a leak. To find out exactly where the leak is, testing can be done by either helium leak detection or with a thermographic infra-red camera. Leak detection services are usually available locally. Splices can be made, but you will have to remove the flooring and open up the slab, splice, repressurize and patch.0 -
DONT RIP UP YOUR WOOD FLOOR!
IS IT POSSIBLE TO ACCESS THAT AREA FROM BELOW?FROM YOUR BASEMENT OR FROM YOUR FIRST FLOOR IF THE LEAK IS ON THE SECOND FLOOR?
I HAVE REPAIRED THESE TYPES OF LEAKS BY GOING THROUGH THE UNDERSIDE OF THE FLOOR WITHOUT DAMAGING ANYTHING STRUCTUAL,ITS NOT ALWAYS EASY BUT WILL BE LESS COSTLY THEN REMOVING ANY WOOD FLOORS.0 -
Isolating & pressurizing will tell you,,,
if it`s the radiant side,, but if embedded in Gypcrete I would think repairing from below, or ripping up the floor would be a toss-up expense wise.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements