thoughtfulTom
Member Posts: 18
in Solar
Greetings,
I build large residential systems to provide space heating and DHW. We only install drainback systems.
Currently we are using atmospheric tanks (plastic or EPDM lined). I am able to seal these, but when the water comes back as steam, the increased pressure blows my seals and I get a steamy room. I could use the controller to limit it, but with solar you want every BTU you can get. This only results from stagnation conditions, but in the fall and spring we might satisfy the tank by noon and want to top it off at 3pm.
So I would like to be able to handle the 1-2 minute steam bursts when they happen. I am considering making a still like cooling tower out of 1/2" copper, then taking that through a 1/2 trap and then wasting any remaining steam outside. Anyone solved this problem?
thanks,
Tom
I build large residential systems to provide space heating and DHW. We only install drainback systems.
Currently we are using atmospheric tanks (plastic or EPDM lined). I am able to seal these, but when the water comes back as steam, the increased pressure blows my seals and I get a steamy room. I could use the controller to limit it, but with solar you want every BTU you can get. This only results from stagnation conditions, but in the fall and spring we might satisfy the tank by noon and want to top it off at 3pm.
So I would like to be able to handle the 1-2 minute steam bursts when they happen. I am considering making a still like cooling tower out of 1/2" copper, then taking that through a 1/2 trap and then wasting any remaining steam outside. Anyone solved this problem?
thanks,
Tom
0
Comments
-
drainback stagnation
in a drainback the collectors should be empty and dry when the pump is off. How are you getting steam? When they first fill up and the collector is hot?
This is where a pressurized drainback works so much better. Keeping pressure, even 20PSI raises that boiling point to 259F. It also helps keep some pressure on the pump(s).
Limited application for plastic tanks in solar, as you are seeing.
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Have to pressurize
If you get any flashing then it is best to go to a pressurized drain back.There was an error rendering this rich post.
0 -
seems like pressurizing
would be a good fix. you could still use your large plastic/EPDM tanks if you had a separate drainback reservoir (small water heater?) feeding a coil HX in the big tank.
Roy0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements