becket heat manager and setback thermo
Options
MikeB_3
Member Posts: 2
Can both of these be used? I was told by a local oil man that a setback thermostat shouldn't be used with a Becket heat manager. That (also) then wouldn't really save much of anything,...
0
Comments
-
My 2 Cents
I have a number of customers we have installed both the Heat Manager and Honeywell Pro 4000 (programmable set-back) Thermostats together. They are working just fine and our customers have been enjoying the comfort and savings we’ve provided them with.There was an error rendering this rich post.
0 -
Absolutely!
The HM only holds off the burner.With a deep setback,it may take a little longer to recover,but I have dozens installed w/ no problem.I put one in today, actuallyTo learn more about this professional, click here to visit their ad in Find A Contractor.0
This discussion has been closed.