Carlin 702CRD help
GW
Member Posts: 4,843
in Oil Heating
Hello,
I do mainly residential stuff. I may be adopting an oil Smith 9A-9 section with a Carlin 702CRD. I spoke with tech support and they were very helpful.
As far as spare parts to have on hand, can anyone give me some input as to what I may want to have on hand for the occasional no-heat? It's an apartment complex so I would like to be prepared for the nigh and weekend.
Thanks for any help, Gary
I do mainly residential stuff. I may be adopting an oil Smith 9A-9 section with a Carlin 702CRD. I spoke with tech support and they were very helpful.
As far as spare parts to have on hand, can anyone give me some input as to what I may want to have on hand for the occasional no-heat? It's an apartment complex so I would like to be prepared for the nigh and weekend.
Thanks for any help, Gary
0
Comments
-
What we do
Gary,
What we do is leave a couple spare nozzles on site. We keep a spare igniter/transformer at the shop. We service about eighteen big burners, Powerflame, Beckett, and Carlin. If you have a chance I would recommend going to Carlin's one day class. I went just before Ruthe's party in July.
Leo0 -
A little off topic...
In about 1980, I had a GE burner replaced with a Beckett because parts for the GE were no longer available, and it would leak oil because an automatic shutoff valve just before the nozzle would no longer shut off. The Beckett worked for about 30 years and was still working when I had the almost 60 year-old boiler replaced with a gas one.
The only trouble with the Beckett in the early years was that it ate high voltage transformers. These were about 3" x 3" x 4", if I remember correctly. And every 3 years or so I needed a new one. But after about 3 of those, my service company put in a tiny solid state one that ran about 20 years and was still working when I had the boiler replaced.0 -
I thought of another thing
Gary,
You may want to check the boiler room, some places keep a motor and pump on site. I forgot to mention this when I wrote the last post.
JD
This burner can fire up to 13 gal/hour in high fire. Very different from what you had.
Leo0 -
Leo
Thanks for the help. These boilers are way over-sized. This 9 section is rated at 10.8 GPH. At another building (same building size) we installed two small 1.7 gallon boilers.
So, with that said, what is the lowest you would try with this boiler? Right now the burner has a 4.5 gal which equates to 7.65 GPH. Like I just mentioned, our installation in the same complex is running 3.4 gallons
Thanks, gary0 -
Aquastat
Gary,
Is there an aquastat to bring it back to low fire? Often times this is neglected and defeats the purpose of a two stage burner. Some guys cheat and lock them into low fire but if the building needs heat or if it also does domestic hot water you want the extra btu's of high fire.
Are you using gas boilers or oil in the building with the two small boilers?
Leo0 -
Smith 19A and Carlin 702
Gary,
According to the Carlin OEM Setup-Guide, (Our bible.....) that combination of the Smith 19A-9 with Carlin 702CRD burner, uses a Hago 6.00 by 60degree P nozzle, with the head position at 1" and air setting at 5/8" 100PSI on low fire and 300PSI on high fire. (Dual pressure regulator on Suntec B2TA pump.) My guess is a spare nozzle, coupling, electrodes, oil filter cartridge and possibly a replacement Carlin 60200 primary control. Hope that helps you.
Downfiring this burner on the Smith 19A is possible but be cautious of approaching condensing temps on the stack gases. (Use an ELECTRONIC analyzer) The 702 burner is used to fire a 6, 7, 8 and 9 section boiler so you are at the upper end of the burner capacity on this boiler. That leaves room (mechanically) to allow some down firing. Good luck and be safe and careful.
Jeff Krawic0 -
702 CRD
I service approx. 25 Carlin 702's . The weekest link is the blower wheel,Carlin knows about this and has a kit to replace . It has a fan and new static plate. PITA to install. Next is the pump. the ajustment screw for low fire is under the mod. mtr.Look for it Must remove rubber cap on solinoid valve. Lots of fun. Last is the coupling, its longer than standard 6" King coupling. So I use the heavy rubber one with the teeth and metal ends. Hope this helps ED0 -
damn couplings
As Ed nyc said, get yourself a rubber( Guardian) coupling with the separate metal ends and make sure the blower wheel has been changed over to the heavy duty one.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements