Snowmelt in outdoor stairs
hot_rod
Member Posts: 23,184
It is critical that you have a tube near the front, top edge of the step. Easier said than done. That is a high heat loss area with two exposed edges. Even if the rest of the step is melted a strip of ice on that front edge is still a problem.
1/2" tube, if you keep the loop length short, helps you install with a tight bend to get two tubes per tread, one about 1-1/2 from the top and front edge. Rebar in the steps help keep the tube at that critical point. As well as accommodating concrete installers/ finishers :)
ACI indicates 3 times the aggregrate size over the tube. With a pea gravel mix you are sure to get proper coverage around a tube 1-1/2:" below the surface.
Only one chance to get it right spend enough time forming and suspending the tube where it will do the best job.
hr
1/2" tube, if you keep the loop length short, helps you install with a tight bend to get two tubes per tread, one about 1-1/2 from the top and front edge. Rebar in the steps help keep the tube at that critical point. As well as accommodating concrete installers/ finishers :)
ACI indicates 3 times the aggregrate size over the tube. With a pea gravel mix you are sure to get proper coverage around a tube 1-1/2:" below the surface.
Only one chance to get it right spend enough time forming and suspending the tube where it will do the best job.
hr
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Comments
-
Snowmelt in outdoor stairs
Can anyone help me out with a detailed drawing showing tubing for snowmelting the front stairs of a library? Steps will be made of a wood form, poured concrete, a tubing pass the length of a step and back, and on to the next step. The consulting engineer will not accept my rough drawings and is insisting on a detailed drawing? Ive checked a number of manufacturer's installation manuals and websites with no luck. Thanks, Gary0 -
How is this picture?
See attached file0 -
step detail
Great picture. Unfortunately what the engineer wants is a "cutaway " showing rod or mesh formed and tube attached. Thanks again, Gary0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements