boiler water feed

KevinCorr
KevinCorr Member Posts: 106
I always do. Nice to have the air vent after the new water.

Comments

  • chuck172
    chuck172 Member Posts: 90
    boiler water feed

    Is there any reason why I can't pipe the water pressure regulator and the backflow preventer between the air scoop and the expansion tank?
  • kpc_75
    kpc_75 Member Posts: 37
    That is..

    really the best place for it. That way the fill valve will not pop on at circ. start up.
  • Jean-David Beyer
    Jean-David Beyer Member Posts: 2,666


    Not only is it a good place for it, many air eliminators have a connection on the bottom just for an expansion tank, and at least for my W-M Ultra-3, the installation manual shows hooking up the backflow preventor and pressure reducing valve right in the line between the expansion tank and the air eliminator.
  • chuck172
    chuck172 Member Posts: 90
    Thanks all

    Thank you everyone for your replies.