Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

New steamer

Options
bob young
bob young Member Posts: 2,177
nice job. you might want to tell the home owner to find a better spot to store his paint, etc.

Comments

  • jim s_2
    jim s_2 Member Posts: 113
    Options
    New steamer

    Nice job for a Friday.

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Options
    new steamer

    nice drop header on that one. will there be enough venting capacity with that hoffman [?] 75 on the return?

    i see the dreaded standard honeywell pressuretrol mounted on the boiler-can you set the pressure on it low enough for this system? my experience was that when set as low as it would go, it allowed the pressure to go up to the 10 psi cut-out on the secondary pressuretrol! that was very soon replaced by a vaporstat, set for 2-8 oz.

    i also agree on being careful with close-by starage, not only of paint, but also water-softener salt etc. which may allow chlorides into the boiler, and rot it out, as happened to mine i think.--nbc
This discussion has been closed.