Mass code question
Mad Dog_2
Member Posts: 7,519
which NYS and even NYC is going by now for the most part. Mad Dog
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=299&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=299&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Mass code question
Anybody from Mass. know where in the code it says the maximum water temperature allowed in the sanitary drainage system is 150 degrees?
Thanks,0 -
see 10.12 (4).
iF YOU HAVE DISHWASHER, YOU MUST HAVE COOLER0 -
We have drained dishwashers
indirectly into the side of a floor drain with no problem from the inspectors
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I do
not have my code book here at home but I believe it has to do with boiler blow down. If you don't have an answer by tomorrow morning I'll look it up.
Jack0 -
Same here on vacation no code book
But I also believe it is a boiler related issue.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
MA has it's own code. I thought it was 150 degrees also but i can't find it anywhere other than the section about boiler blow off tanks which is in 10.21 1 (b)
http://www.mass.gov/?pageID=ocaterminal&L=6&L0=Home&L1=Licensee&L2=Division+of+Professional+Licensure+Boards&L3=Board+of+State+Examiners+of+Plumbers+and+Gas+Fitters&L4=Statutes+and+Regulations&L5=Rules+and+Regulations+Governing+Plumbers+and+Gas+Fitters&sid=Eoca&b=terminalcontent&f=dpl_boards_pl_cmr_248cmr1000b&csid=Eoca#10.15
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
What's the point?
About an hour ago my wife drained boiling potato water down the drain. She remarked again that Martha Stewart said to add cold wter to boiling water to protect plumbing.I was wondering if the pipe makers thought of this! What is the premise of the Reg.?? Enjoy the 4th. Our very own Sarah P. quit today.0 -
Mass code question
248 CMR section 10.21 Boiler blow-off piping
(1) Boiler Blow-off Tank. (See 248 CMR 10.22: Figure 1: Illustration of Boiler Blow Off Tank). A vessel designed to receive the discharge from a boiler blow-out outlet and to cool the discharge to a temperature of 150deg F or less which permits its safe discharge to the drainage system.
(1)(b) The temperature of water entering drainage piping from discharge of blow-off equipment shall not exceed 150degF.
(2)(a)2. Such waste water when it is discharged into a building drainage system shall have a temperature of not more than 150degF.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements