OK to drill and tap a 3/4\" main vent hole on a 3\" iron main?
bob young
Member Posts: 2,177
YEAH, Dave baby.......for a small fee.
0
Comments
-
OK to drill and tap a 3/4\" main vent hole on a 3\" iron main?
On my one-pipe steam system I have a long main with no vent. The options for adding a vent seem to be drilling and tapping, or else adding a "T". The main is one long pipe, so I'm guessing that adding a T would involve cutting and threading, which I'd like to avoid. AS my question indicates, I'm assuming that a 3/4" nipple off the main would be the proper size for the main vent. Thanks!0 -
drill and tap a 3/4\" main vent
I`ve seen it done, but personally I`m leery of-it without having a "boss" arc-welded to the pipe.
I have D&T smaller holes up to 1/2" in 3" pipe though.
Dave0 -
weld it
weld -o-let [ boss ] as dave suggested is the way to go. a first class permanent job.0 -
You can tap much smaller than 3/4 inch.
You can tap a 1/8 inch hole and then increase to 1/2 or 3/4 for a main vent. A short 1/8 inch pipe flows the same amount of air as the largest main vent avialable... the Gorton #2.
Boilerpro
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
I'd use
several smaller tappings- 3/4" is getting big enough that the walls of the pipe being tapped might not be thick enough to provide enough threads to support the vent pipe. If you must use a single 3/4" tapping, have a thread-o-let welded on as Dave and Bob suggest.
But several 1/2" tappings would probably work great.
I'd use something bigger than 1/8" for the Gorton #2. I prefer 1/2" for this vent to keep the steam velocity in the vent pipe down. But when using a Gorton #1, which is smaller, 1/4" or even 1/8" would be fine.
How long is your 3" main?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
The main is approx. 25' long. Thanks for these answers!0 -
A Gorton #2
will vent that main quickly, at just over an ounce of pressure. You only need to tap 1/2" for it.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I'm an idiot, the main is actually 2\", not 3\". Does that change
the answer?0 -
2\" is pretty small to tap \"period\".
you may get away with a 3/8" hole,, or 2 different 1/4" ones.
It gets touchy with 2"!
With a 4 wheel pipe-cutter, a pro can install the proper size fitting you need. :-).
Dave0 -
bob,
"IF" it was my house, I would no-doubt try-it,,, but then again, I have the tools to fix-it if things didn`t work out.
As you know,, 2" can be very touchy to D&T if not experienced. ;-)
Dave0 -
In that case
use two Gorton #1 or Hoffman #75 vents (though the Hoffmans are more expensive). The 1/2" pipe mentioned above will do nicely. I've drilled and tapped for installations like this many times with no problem.
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
[ the edge factor. ]
YEAH but you got the edge, dave 'cause you know if you can't fix it me & paul bunyan will come over to your house & slap in a new main F.O.C. [ free of charge. ] we will also bring a cooler full of beck's dark so the job goes extra smooth.0 -
Sorry I missed your post old friend,
not much of a beer drinker myself,,,white-rum & Pepsi is my preference. :-)
Dave0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements