Triangle Tube prestige E02 errors

tim smith
tim smith Member Posts: 2,807
I am starting to see a few issues with TT E02 errors. Still not sure exactly what problem is. We find a little build up on electrodes, some warping on electrodes. Combusiton #s good. Gas pressure good. But still happens periodically. What say others about this, anyone else seeing a bit of a pattern?? Still love the boiler but just wunderin. Tim

Comments

  • Kal Row
    Kal Row Member Posts: 1,520
    airflow!!!

    all sorts of stupid stuff, like debris in the intake or the exhaust, or the heat exchanger – to a backed up condensate trap – (just had one of those on a Lochinvar and the float-sw in the trap was stuck – so it’s smart display kept quiet) – if you live around the eastern seaboard – we’ve had an unusual wet season you could have water in the intake or exhaust – or if the exhaust goes horizontally for a long distance and sagged in the middle – it could collect water and block – happens a lot when the cellular foam core pvc is used instead of solid – lots of times – it’s the ac contractor that runs the pvc instead of the boiler installer and they screw it up

    on day – hopefully soon, all the modcon manufactures are going to wake up and realize (like the car people realized a long time ago) that basic flame and pressure sense is bogus, you need to measure real mass airflow, and exhaust O2 levels to know what’s really going on – eg – it you have X RPMs but the airflow is not there, then you have a blockage – if it’s only a partial block then you can alarm it, mod down the boiler, instead of just locking it out, it’s not rocket science

    trouble is, that a MAS (mass airflow sensor) costs them about $120 and an o2 sensor about $35 – and would add about $500 to the retail cost

  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    Every E 02

    I've had was because someone turned off the gas to work on something else without turning off the boiler. Don't discount stupidity. Stupidity happens. WW

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    mknmike
  • Devan
    Devan Member Posts: 138
    My first E02

    Just went thru this on a Excellence. Touchy light ups, sometimes resulting in E02. Checked everything, and replaced ignitor just in case. Checked ground wires from ignitor. After quite a bit of time, and a call to TT with no resolve, noticed on attempts to light up manometer reading dropping out each time then going back to @11" w.c (LPG) .

    It ended up being a bad 2 month old new regulator . Call to gas co. replaced, all's well.



    K.I.S.S.
  • scott_r
    scott_r Member Posts: 1
    TT E 02 problems

    I am having problems with E 02 errors on my new Triangle Tube Solo 60.  It seems to happen like this:  The boiler will ignite and heat my indirect hot water heater.  Once the hot water is satisfied, the boiler shuts off.  Then, if I use hot water soon after (say within 15 minutes to an hour) and the boiler needs to turn on again, then the E 02 message happens.   If I don't use any hot water and the boiler stays off for over an hour or so, than everything is ok. 

    Not sure if this happens when modulating for heat, or if it is just related to hot water.

    Any ideas? 

    Anyone else having E 02 problems?  Tim, did you ever find out the cause of your E 02 problems?
    mknmike
  • Presley
    Presley Member Posts: 1
    Water heater

    I too have a problem with the Excellence boiler shutting down after firing up the water heater, silimar to scott_r. It started after the boiler guy bled the system and turned some of the parameters up. I turned the water parameter back down to 140 degrees. Now when one showers there's a good chance the boiler shuts down with the E02 error either at the end of the shower, or sometimes in the midst of a longer shower. I haven't noticed the heat by itself ever turning the boiler off. The boiler guy claims it has nothing to do with him. What is the probable cause and solution?
  • Gordan
    Gordan Member Posts: 891
    edited January 2012
    There was a technical bulletin recently

    Some newer versions of the MCBA (boiler controller) had issues with ignition, especially on propane. See this thread:



    http://www.heatinghelp.com/forum-thread/138065/Triangle-Tube-PE110-problems