    Munchkin - 8 flashes

    This is on an older 140M unit - pre-925 controller. The 8 flashes on the green light on the circuit board tells me it's the fan or the pressure switch, but both are fine.

    Aside: this unit has had two replacement fans, the last one about 2 years ago; I tested for CO inside the enclosure and none was found.

    The owners have to flip the disconnect every day or so when they have no hot water; it works for awhile and then slips into lockout.

    Any ideas? Bad circuit board?
  • Paul Rohrs_4
    Paul Rohrs_4 Member Posts: 466
    Options
    Concentric Vent?

    Alan, does this have a concentric vent on it? I had a similar experience with a "radiant rescue" call and the culprit was an improper concentric installation. High winds caused a lot of back pressure on the exhaust, not allowing the pressure switch to "make". Try disconnecting the intake for a short time to see if it will still go to the 8-pulse fault.

    Nothing better than hydronic CSI in the summer.

    Regards,

    Paul
  • Jr_12
    Jr_12 Member Posts: 38
    Options


    The pressure Switch could just be getting weak. I would suggest upgrading to the digital board though. The new board will have the longer post purge on the fan, which will help if there is a negative pressure issue in the building.
  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    Options
    New board

    The new 926 board has a much longer post purge. The 140 has a problem that after it shuts off heat would rise from the HX and melt stuff in the flu blower. The new board runs a 90 second cool down so the HX cools enough so that wont happen. Upgrade both refractories while you're at it. It makes for a nice upgrade. The new board also raises the voltage to the flame sensor and makes the sparker a second flame sensor. Say goodbye to any F-09 problems.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • S Ebels_2
    S Ebels_2 Member Posts: 74
    Options
    Had the same thing Alan

    A 140 we installed in 02 IIRC. After troubleshooting everything, and I mean complete disassemble, cleaning, tuning,flame sensor, pressure switch we still had the lockout problem. Chuck told me that the cure would be a board update to the 926 and he was right. Installed it and the boiler runs fine. In fact better than it ever did. It lights off at a little higher fan speed/input and then modulates down to minimum which really makes a difference in reliable starting. Modulates better, steadier fan speed during operation, flame sense reading in the 12-14 UA range. Lights up and stays lit just like it should. It really wasn't all that expensive as boards go.
  • Alan(OnVacationInOregon)Forbes
    Options
    New Board

    I like that longer post-purge feature. And the refractory replacement makes sense. Thanks, guys.

    Nice to see some of my old friends on the board.
  • Steve Ebels_3
    Steve Ebels_3 Member Posts: 1,291
    Options
    It's actually

    A full update kit with new sensors and other fun stuff along with the board.