Flexible pipe connection

hot_rod
Member Posts: 24,726
have a product, or can they recommend one? I have seen braided stainless steel hose used on those and also hydraulic applications, but O2 ingress would be a concern.
A local contractor used a auto parts store MPH (multi purpose hose) heater hose, on a school project once. It didn't work out so well! They did replace them with a braided product of some sort.
hr
A local contractor used a auto parts store MPH (multi purpose hose) heater hose, on a school project once. It didn't work out so well! They did replace them with a braided product of some sort.
hr
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream
trainer for Caleffi NA
Living the hydronic dream
0
Comments
-
Flexible pipe connection
I am plumbing a geothermal unit into a radiant floor heating system. The geothermal guy says to expect movement in the unit and suggests having a flexible connection. On the pipes that are too large for Pex what should I use? I've thought about high pressure rubber hose, but still trying to find out compatiblity with glycol and oxygen barrier qualities. Any ideas?
0 -
Metraflex
Has a wide variety of options for flex connectors. They are often spec'd for commercial projects
Rich0 -
Hose attachments
After reading this thread I am wondering about O2 barrier. I have used both the braded connectors and rubber hoses and it never occured to me that I should think about an O2 barrier. I just asked my geo designer and he thought an air elminator would work if it does not have an O2 barrier, but I have first hand saw what non O2 barrier tubing can do to a radiant system. Does rubber permit air transfer? I think so because I have to pump up my bike tires often to maintain pressure....just some thoughts.
What are your thoughts.
Jeffrey0 -
I don't hear of
corrosion issue with ground source equipment like we do with hydronics. I know temperature plays a large role in O2 ingress, perhaps that is a big part of it?
An air separator, even a great one, will not remove the O2 molecule.
Chemicals are another way the scavenge O2 but need checking and boosting.
In theory an aluminum layer in a rubber or EPDM hose should be a 100% O2 barrier. But...
Maybe a pex/ aluminum tube would be enough flex? Viega FostaPex has the best of all worlds in that respect.
hrBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
metraflex baby
Thanks for the tip on Metraflex. I ordered up some copper ones with sweat ends and they are just poifect. See pic0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 949 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements