Steam run-out
Joe Blanks
Member Posts: 10
Hi all,
If I want to relocate a steam rad on a one-pipe system 7' away, do I need to increase the size of the run-out? The main is 2" with an 1-1/4" run-out to a 54s.f. radiator. The rad will be moved about 7' from the main to the new riser (for 1st floor radiator). What pitch should I use? 1/2" per 10' or 1/2" per foot? The riser is NOT dripped.
Thanks-
If I want to relocate a steam rad on a one-pipe system 7' away, do I need to increase the size of the run-out? The main is 2" with an 1-1/4" run-out to a 54s.f. radiator. The rad will be moved about 7' from the main to the new riser (for 1st floor radiator). What pitch should I use? 1/2" per 10' or 1/2" per foot? The riser is NOT dripped.
Thanks-
0
Comments
-
If you can get
1/2" per foot of pitch or thereabouts, an 1-1/4" riser should be OK.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0