Steam Convectors
Bruce L.
Member Posts: 9
I need to know if steam convectors can be converted to hot water with no modification.
0
Comments
-
yes
pipe sizing might be different [ smaller ] . use bushings0 -
The convectors i see have round tanks on either end0 -
The modification
may be done for you....... leaks.
Remember that if you convert a steam system to hot-water, you will raise its working pressure 10 times or so. If there are any weak points in the piping or radiation, they will leak and possibly damage the building. Then will come the lawyers...............
Also, the existing convectors may not be able to heat the building on hot-water. The building will not heat well on colder days, and then will come the lawyers.........
And the return lines may not be big enough to handle the needed volume of hot-water. Again, the building won't heat well..........
And, if these convectors have built-in orifices, they will whistle as the hot water tries to flow thru them. The customer won't be able to sleep, and then will come the lawyers.....
Our company does not recommend or perform this type of conversion, and will not work on a system someone else has converted. There are just too many liability risks.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements