strange steamer...
kpc_73
Member Posts: 26
at a steam boiler replacement this afternoon. The boiler was a original Weil/ Mclain coal steamer converted to oil that had 380 sq. ft. of steam....about 1946 install.
I looked at the radiation and it had some CI baseboard that had been added some time later. It had some long runs 13 and 17 feet and hada set up of swing checks to keep the steam going in the right direction...This was added to the house w/ an addition sometime in the 50's. Seems to have worked for a while w/o much issue. Here is the really strange thing. The connected load is 489 sq. ft... Piping in the basement is not insulated... And it heats ok...
What does this say about the IBR calcs...Do I go by the connected load or play w/ it a bit and "downsize"?
I looked at the radiation and it had some CI baseboard that had been added some time later. It had some long runs 13 and 17 feet and hada set up of swing checks to keep the steam going in the right direction...This was added to the house w/ an addition sometime in the 50's. Seems to have worked for a while w/o much issue. Here is the really strange thing. The connected load is 489 sq. ft... Piping in the basement is not insulated... And it heats ok...
What does this say about the IBR calcs...Do I go by the connected load or play w/ it a bit and "downsize"?
0
Comments
-
connected load
Is the baseboard in the basement on a aux. loop ? or part of house load w/ two pipe supply & return piping.0 -
Baseboard....
is steam...all tied into the main headers.0 -
actual oil output?
getting higher output (SF) from oil than it originally did from coal, were the coal ratings were conservative, for variation in fire quality?
EDR is lower than you think -- metallic painted radiators, slow venting (rads and mains) so radiators don't fully heat, but still exceed structure losses, error in radiator table for radiator/convector type, etc.?
What's the current oil firing rate and combustion efficiency while steaming, this would give actual gross output.0 -
the standard sizing methodology
is going to work 100% of the time in 100% of the situations..so that does imply some degree of oversizing..there are numerous instances where the IBR method oversizes..but i'd size to the IBR and install stage firing controls.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements