Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Prestige 110 vent supplement?

tim smith
tim smith Member Posts: 2,807

Comments

  • tim smith
    tim smith Member Posts: 2,807
    Prestige 110 vent supplement ? Tim Smith

    Hey guy's I cannot find our vent supplements and there is not one online. Anybody have one they can email me or look and tell me what the clearance on termination is to the side of a operable window. I need to finish bid today and have to know this. Thanks, Tim
  • John Starcher_4
    John Starcher_4 Member Posts: 794
    From the supplement:

    "Vent terminations must maintain the following clearances:

    a. At least 6 feet from adjacent walls
    b. No closer than 5 feet below roof overhangs
    c. At least 7 feet above any public walkway
    d. At least 3 feet above any forced air intake within 10 feet
    e. No closer than 12 inches below or horizontally from any door or window or gravity air inlet
    f. Must be at least 4 feet from any electric meters, gas meters, relief valves or other equipment. Never terminate the vent above or below any of these itiems within 4 feet horizontally
    g. A maximum of 12 inches beyond the exterior wall
This discussion has been closed.