Prestige 110 vent supplement?
tim smith
Member Posts: 2,807
0
Comments
-
Prestige 110 vent supplement ? Tim Smith
Hey guy's I cannot find our vent supplements and there is not one online. Anybody have one they can email me or look and tell me what the clearance on termination is to the side of a operable window. I need to finish bid today and have to know this. Thanks, Tim0 -
From the supplement:
"Vent terminations must maintain the following clearances:
a. At least 6 feet from adjacent walls
b. No closer than 5 feet below roof overhangs
c. At least 7 feet above any public walkway
d. At least 3 feet above any forced air intake within 10 feet
e. No closer than 12 inches below or horizontally from any door or window or gravity air inlet
f. Must be at least 4 feet from any electric meters, gas meters, relief valves or other equipment. Never terminate the vent above or below any of these itiems within 4 feet horizontally
g. A maximum of 12 inches beyond the exterior wall0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements