derating a Revolution
KBP&H_3
Member Posts: 67
I also passed this Q to Burnham as I have a RV5,- the house addition was 600 sq ft less than anticipated).. Anyway, Burnham said not to change anything as the co2 and the p vent fan, and input are all related,, There is a baffle / orfice plate before the blower that is different sizes between the different boilers. They also said that the boiler needs to have a consistent temp across the cast iron.. There is also the manuf rating and warranty, I'd like to also down rate it.. but there seems to be more variables.
0
Comments
-
derating a Revolution
The boiler in question is a Burnham Revolution RV-4. Serves two zones of fin-tube at a design load of around 33-35k BTU/hr at ~140F supply, and a 40 gal State Escort indirect which receives preheated water from a solar DHW system. It never has to do more than a 50F rise on DHW calls.
Control is a tekmar 260 with indoor feedback.
On space heating calls, the boiler never runs more than 5-6 minutes, or less than 4. Not short cycling, but not long, either.
Am contemplating having the orifices changed to reduce the input from 96k BTU/hr to something less. Perhaps up to the 20% derate allowed by code. 77k BTU/hr would still be plenty to do the 50F max rise needed for DHW, and also lengthen the runtime on space heating calls.
Is this a reasonable idea, or unnecessary?
Alternatives include a) do nothing, and b) implement a buffer tank. Using Siegenthaler's formula for buffer tank sizing, something in the 50-60 gallon size would give a long runtime and a long off-time.
Thanks for any thoughts.0 -
aking them
Have a query to Burnham as well. Good considerations, those. But I would think that an orifice change would at least not affect the temperature across the hx. If anything, the longer runtimes would allow more even and lengthy warmth.
Thanks.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements