Heat Loss Calc Results - Can I use to Size air or radiant heat?
Big Ed_4
Member Posts: 3,020
You use the total heat loss for the size boiler or furnace Then do a heat loss per room for size of radiation, duct size or radiant loop...
Heat gain total for AC system , per room for duct size ...
Your on the right track ....
Heat gain total for AC system , per room for duct size ...
Your on the right track ....
There was an error rendering this rich post.
0
Comments
-
Heat Loss Calc Results - Can I use to Size air or radiant heat?
working on the design of a hydronic radiant heat system for my expanded 1920's house. as an engineer and renovation pro I am designing the system as much as I can so subs can bid on apples to apples system install.
question - i've used tlhe hvac calc program and developed heat gain and loss calcs that I feel pretty good about the data input (wall construction, insul., windows, exposure, ceilings, fireplace, people, stove, infiltration, design temp., etc.).
is there any reason that I shouldn't use the same btu's/hr in heat loss per room/level/zone to size the radiant piping heat delivery system (and thus water temps, supply pipes, and circulator selection to the rooms/zones?
i realize the radiant heat curve and net radiant temp. in the room has a bearing on comfort - but do I not need to deliver the same btu's to the room whether it's forced air or radiant- and thus can use my heat loss numbers to guide that radiant design?
is there an alternative program I can download (for heat loss calcs for a radiant system) or alternatively to help me size and distribute pex loops, supply pipes, etc. based on the house's heat loss that I've calculated?
thanks alot for any advice!0 -
thanks Big Ed.
so - if I've got 'x' btu's /hr. loss in a particular room - then I need to get 'x' btu's per hour in there on a design day - either by 'y' cfm of furnace hot air, or by 'z' gpm at 't' temp. through pex under the floor? in other words btu's are btu's - though the radiant delivery of the btu's should provide more comfort/less drafty feeling/more 'apparent' heat from the radiant xfer of the heat from the floor and heated objects.
does this sound right?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements