where is the best place to put the cold water feed on a steam system?
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    return

    it should be as far down the return as can be, so the cold water can be mixed up with the return water.--nbc