Plumbing Question -OT

bob young
bob young Member Posts: 2,177
BACKFLOW IS SERIOUS BUSINESS

Comments

  • JJ_4
    JJ_4 Member Posts: 146
    Plumbing Question..OT

    I have a quick plumbing question. We have a cleaning product mixing station attached to a faucet at the slop sink. The faucet has a vaccum breaker built in. Is this sufficient (to code) for backflow prevention in a commerical building?

    Thanks
  • JK_3
    JK_3 Member Posts: 240
    most codes

    Yes a vacuum breaker commercial faucet is acceptable backflow prevention in New York City in most applications and to the best of my knowledge we have the toughest codes.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"

    There was an error rendering this rich post.

  • Billy March_2
    Billy March_2 Member Posts: 57


    The built in vac breaker is all that is required to meet code. An RPZ is an added bonus but not required on a mop sink faucet.