Pump to Maintain a fixed delta T
Garritt
Member Posts: 27
Taco makes a varible speed pump based on delta t.
0
Comments
-
scratching my head
How do you run a variable speed pump to maintain attempt a fixed temperature differential between two sensors, AND run only if one is larger than the other.
say sensor A is on system return, sensor B is reading the outlet of a solar tank, and you shoot for a ten degree optimal differential. As long as A is less than B, the pump runs (powered up by a heat demand, or constant circ, your choice), ramping up in speed as the differential grows to full power at your specified differential.
I know there must be something out there that will translate a temperature differential to a variable power output....0 -
Why?
You want a control that turns on at a specified differential and then increases pump speed to a set higher differential? ie 40Hz at 5°F differential and 60Hz at 30°F differential? Then if the differential drops below 5°F it shuts off? I'm not sure I follow why one would do this? Why is the differential important?
Could you use a differential setpoint control to kick on the circ and then use a Wilo Stratos on dT control? I haven't used a Stratos, so I'm not completely sure on all of the control options included.0 -
Wilo Stratos
The Stratos can accomplish this via a 0-10 vdc signal and our 0-10vdc module.
Honeywell makes a control that will modulate the signal based on DT and this will ramp the pump up and down accordingly. I am sure there are other control companies that make similar devices and I do not mean to leave anyone out.
Feel free to contact me if you have further questions.
Mark H
0 -
Maybe
Resol has a line of solar controllers that use a differential to run a variable speed pump. Not sure if they are available in the US. I use the fixed relay version. Here's one link:
http://www.acmegreen.com/page4/assets/Resol_Solar_Controller.pdf0 -
Rob
What flow rates are you looking for. Are we talking a OO series Taco variable speed or something larger?0 -
doing a solar contribution tie in with a differential control reading the outlet temp of a solar coil, and the return temp of a heating system.
if outlet is higher than heating, transfer.
Problem is, when you transfer on full speed, the sensor temperature plummets, and it kills transfer pretty fast. I am suspecting that a delta-T control pump might prevent that "see saw" and instead allow for a more consistent draw from the solar tank. Worst case, another option for the problem is that the tank "flips" when we draw a lot of heat out very fast, and a delta-T control might fix that too...0 -
very low flows desired. Negligable frictional loss and low, perhaps even fractional GPMs at times.0 -
Thanks for the help mark and pexrunner!0 -
I'd look at the OO Taco VS first although I don't know how low it will go. Wilo would be high on the list also.0 -
thanks! we're checking it out: seems like it might be a decent fit.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements