Looking for Kewanee Boiler Info
bert
Member Posts: 50
I have some info on hand. What is the nameplate info?
0
Comments
-
Re-tube job
I have a customer that wants a price on completely re-tubing an older Kewanee boiler. I'm having trouble finding information about what tube material to use with Kewanee out of business. I have all of the info off of the plates. Any info is greatly appreciated.
Thanks, Rich L0 -
Re-tube
Check with Burnham, I heard a rumor that they bought Kewanee...0 -
Burnham's busy
Wow, on hold for over half an hour. I can't get through to them.0 -
Burnham is closed today!!0 -
Tube
probably .095 wall carbon steel. Do you have an R stamp ? a lot of states require an ASME R stamp to retube a boiler.There was an error rendering this rich post.
0 -
Explains that!
0 -
Name Plate
This is all the information I have off of the name plate on the jacket and under the cover right above that there's another plate directly on the boiler shell itself.
Manufacturer - Kewanee Boiler
Year built - 12/73
Model - 7L287 ("H" Stamp)
Serial # P-0526
WAS7l285KG0
Date 3-28-73
53462IA
Max steam 15 psi
Max water 30 psi
I429HS
VCII432LB
I973
9800
Thanks for all the responses and any help. Rich L0 -
Another Quote
my customer received called for 3" OD x 12 guage SA178A tubes. My boss won't let me run with that, what if they were wrong? Once we re-tube it we own it, if anything were to go wrong anyway.
Standard "Carbon Steel" won't cut it either. We've got to use the same materials spec'd by the manufacturer, even though they're not around any more. If I'm wrong on this please feel free to correct me. You'd save me a lot of work! But tell me where I can find the documents to back it up.
Yes, our shop has an "R" stamp.
Thanks again for the help.0 -
follow up
84 direct tubes, 3" od, .105 wall, 10' - 3-3/4"
60 return tubes, 3" od, .105 wall. 12' - 2"
note .105 wall is prox. 12 ga, field verify lenghts
lengths shown include 1/2 to 1" for beading or flaring
use min. A106 or better
American Tube & Iron will have tubing in stock0 -
Thanks Bert!
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements