UPS 40 80 / 2 amps?

Timco
Timco Member Posts: 3,040
I have 6) 40 80 / 2 grund circs on a single 20 A ckt. This setup is run through a tekmar 046 10A relay which cooked very nicely. What is the draw per circ? Wondering if a 20 A relay would do it or do I need to put 3 circs on one pole and 3 on another to even this out...

Thanks, Tim
Just a guy running some pipes.

Comments

  • AMPS on UPS 40-80/2

    Hi Tim... Assuming it's 230/1 and running on speed 3 starting amps is 5.6 and running amps is 2.24.

    You can avoid the starting surge by using a Stratos (soft start). Sorry for the plug but when an opp comes up...