academic question
Steamhead (in transit)
Member Posts: 6,688
so the water lines will be the same.
Size your headers generously and pipe them similarly, to reduce pressure drop and equalize it as much as possible. Run your boiler headers into a common header, then feed the common mains. See the diagram on page 67 of "The Lost Art of Steam heating".
If your boilers need more than one riser to the header, a drop header makes the job easier. Maintain your 24-inch riser height from the highest possible waterline as usual.
If you're going to stage-fire these boilers, put a Vaporstat on the common header and wire it to stop the smaller boiler when the pressure reaches a few ounces.
Dirty boiler water will cause a lot of back-and-forth flow between the boilers. Leave a lot of nipples and caps for flushing and skimming.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Size your headers generously and pipe them similarly, to reduce pressure drop and equalize it as much as possible. Run your boiler headers into a common header, then feed the common mains. See the diagram on page 67 of "The Lost Art of Steam heating".
If your boilers need more than one riser to the header, a drop header makes the job easier. Maintain your 24-inch riser height from the highest possible waterline as usual.
If you're going to stage-fire these boilers, put a Vaporstat on the common header and wire it to stop the smaller boiler when the pressure reaches a few ounces.
Dirty boiler water will cause a lot of back-and-forth flow between the boilers. Leave a lot of nipples and caps for flushing and skimming.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
steam boilers
the questions is this: installing two steamers (<2 psi) side by side to a common main, they are physically dissimilar and of unequal firing rate. Are there any installation requirements (code, otj experiences etc) that dictate? Maintain the 24 inches from nowl to header etc? Use drop headers? thanks0 -
thanks
that is exactly what I needed.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements