Anti freeze for solar

mark s
mark s Member Posts: 12
Thanks for all the info.
I am in NE PA and trying to find a product my local supplies will stock.
This is becoming a project just to educate them on solar systems.
Has anyone used a tankless coil on an oil boiler as a dump for the system?
I am using a PAW flowcon C+ station and 3 way valve with a 30 tube collector and 80 gallon Vaugh solar tank.

Comments

  • mark s
    mark s Member Posts: 12


    What manufactures make anti freeze rated for a closed loop vacuum tube a domestic watermheating system? PH needs to 8.
  • Paul Pollets
    Paul Pollets Member Posts: 3,661
    Either...

    Viessmann Tyflocor (pre-diluted to -20 protection) or Dow Frost (Undiluted)

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • hot_rod
    hot_rod Member Posts: 22,830
    For evac tubes be sure

    you select a HD, heavy duty fluid. These have higher operating temperatures, better inhibitors.

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Mike C._4
    Mike C._4 Member Posts: 56
    solar antifreeze

    There's also Noble and Rhomar (which I use) as many others. You need to use the propylene glycol HD versions (if incidental potable water contact is an issue) i.e. the ones with the more inhibitors in them. Don't use automotive type. Ironically, most are rated for up to 325 deg F and not recommended for evac tube installs but there isn't much for a choice. I am not sure about the Tyfocor specs. 50% max mix should be about -28 deg F. Use the least protection that will do the job. It will help with heat transfer and pumping. Clean your system good and if you mix use distilled water.

    Mike
  • mark s
    mark s Member Posts: 12


    Thanks for the info. My local supply house quoted Rhogard05 but is waiting for a call back from supplier if this will be ok to use. Does anyone know if this is ok for solar?
  • RhoGard in solar

    The RhoGard should be ok for your solar system, especially if it contains aluminum or copper. You don't want to use DowFrost with aluminum.

    Rhomar also has a glycol similar to DowFrost called EnviroGard ST. It would probably cost less then DowFrost. The EnviroGard has food type ingredients in case you are concerned about potable water contamination.

    Dwight
  • Drew_2
    Drew_2 Member Posts: 158
    Antifreeze for Solar

    Here is a breakdown of some Solar antifreezes. Dow HD and Noburst HD are propylene glycol based. Tyfocor is potassium formate. Propylene glycol is GRAS(Generaly Recognized As Safe) as a food product by the FDA. Potassium formate is not GRAS. All the ingredients in the Noburst HD formula are GRAS.
    These issues are important in some areas of the U.S. when solar is used for domestic water heating with a single walled system.
  • hot_rod
    hot_rod Member Posts: 22,830
    the fluids designed

    for high temperature evac tube applications may not pass the FDA approval, as Drew mentioned. Best check that out with some of the import fluids.

    This is the type of thing that could give solar a black eye and force more codes to re-examine double walled heat exchangers. Seems just when the double wall restrictions were being re-examined and lifted in areas, along comes another reason for code officials to question solar fluids.

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Larry C_13
    Larry C_13 Member Posts: 94
    DowFrost and Aluminum

    What is the issue with DowFrost and Aluminum? I used DowFrost in an application with aluminum blocks that are being chilled down to about 10 F.

    Larry C
  • Larry C_13
    Larry C_13 Member Posts: 94
    DowFrost and Aluminum Part II

    After talking to Dow, the issue is above 150 F, the inhibators start breaking down.

    Larry C
  • hot_rod
    hot_rod Member Posts: 22,830
    tankless coil

    dump is a clever idea. Again, it may not be needed if you have a good year arounf DHW load. That cast boiler could absorb some excess, but it may warm the space where the boiler is located :)

    hr
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • mark s
    mark s Member Posts: 12


    I am hoping to get some free btus in the winter by using the tankless coil.We are not home during the day and after we charge the tank we should be able to send that
    extra heat into the boiler.
    If I set the collector to the winter angle I may not over heat the boiler room in the summer. This is all new to me and I may as well experiment on my own system.