Dry return question
1974 bobcat
Member Posts: 6
I went out to look at a steam boiler that another mechanic installed. I saw something questionable and (just for my own knowelege) wanted to get a few opinions. On a steam boiler (one pipe system)that has several dry returns they usually have a vent near the end and then drop to below the water line, in kind of a return header.
On this install the mechanic tied the two dry returns together in the ceiling ( increased the size)and then droped below the water line.
Is that ok?
It seams to me that the old timers droped those returns individually for a reason. I've been told that it is ok
Thanks, Bob
On this install the mechanic tied the two dry returns together in the ceiling ( increased the size)and then droped below the water line.
Is that ok?
It seams to me that the old timers droped those returns individually for a reason. I've been told that it is ok
Thanks, Bob
0
Comments
-
Individual drops
were there to keep steam from going from one return line to the other. Dropping them below the waterline prevents this.
Does this system have main vents?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
reply
yes, it has 2 main vents and then it ties together and drops.0 -
You need
a second drop, then connect them below the waterline.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks for the advise, I thought that there was something wrong with the way it was piped. I fixed it today and now all the radiators heat.
The way it was tied in allowed the pressure to equalize an not much steam left the boiler, actually it was short cycling. It is all better now.
thanks bob0 -
Great!
and I'll bet their fuel bill goes down a bit, too.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements