retro
don_205
Member Posts: 66
You left out the head.You made get 15 gpm out of it if the pump was only seeing 5 feet of head.
Personally as a service tech I would love to see more differential by-pass valves when using zone valves.Nothing like walking up on a zones system with one huge pump and hearing a noise thru out the house when only one zone is calling.
Oh no...its got type m copper and short radius ells too.
Personally as a service tech I would love to see more differential by-pass valves when using zone valves.Nothing like walking up on a zones system with one huge pump and hearing a noise thru out the house when only one zone is calling.
Oh no...its got type m copper and short radius ells too.
0
Comments
-
what would you do ?
I'm still learning this stuff. I don't have much problem when designing from scratch. I run into issues with retrofits. This is for a simple boiler replacement that I'm choosing to over think. here is my situation:
I have 3 zones that are high temp baseboard. I figured all gpm to be 2 fps
Zone 1 - heat load is 37,259 btu
Supply & return common pipe is 1" that splits into two 3/4" loops
@ 5.5 gpm my DT is 13.5
Zone 2- load @14,688
3/4" loop
@ 3.2 gpm DT is 9.18
zone 3- load @ 16,660
3/4" loop
@ 3.2 gpm DT is 10
A 007 can pump up to 15 gpm so I'm thinking that zone valves may be good. However (if I remember correct) Robert Bean stated that the threshold for using circs over valves is when the zone is over 4 gpm.
Should I zone w/ valves or pumps ?
If I piped both supply & returns into a common header would I make that 1 1/2" ?
0 -
At 12 gpm,
a 007 will push a max. of 7 ft. of head; a 0010 will push a max. 0f just less than 10 ft. of head. Baseboard has a low pressure drop, but since this is a retrofit and you really don't know what's out there in terms of pipe and fitting, I'd go with circs. to play it safe.
0 -
one pump
To take the guess work out of it I would use a Wilo-Stratos ECO and use zone valves or ideally TRV's and do constant flow. The Wilo is a little little pricey but well worth it especially if you did zone pumping.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements