Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
becket heat manager/w setback thermostat
Hollis
Member Posts: 105
I got a Beckett heat manager for a rental unit and installed a set back thermostat. It will hold that temp if given enough time but doesn't seem to work when you hit the overide button on the thermostat. The circulator starts up but the burner doesn't come on for a long time (>an hour) My heating guys (who doesn't seem to like the heat managers) said he called Beckett and according to him said that they don't work with set back thermostats. I never saw this in any of their literature. Anyone know if this is really true?
0
Comments
-
you must
not have it hooked up correctly.
It shouldn't have anything to do with the thermostat.
It interrupts the burner. I have a setback thermostat and it works fine.
http://www.becketthm.com/pdf/7512 rev 6 (HM residential) install instructions.pdf
copy and paste this in your browser... and get a different heat guy.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements