hey frank & other experts
need advice on IN6 Burnham steam. doing 3 " drop header. what is advantage if any to use two supply risers as opposed to one single riser which is mandated in piping diagram. thanks gents.0 -
The advantage is
that the steam velocity as it leaves the boiler is cut in half. This further reduces the possibility of water getting up the risers.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
thanks, frank. you are the best
0 -
thanks again frank.
job came out primo. so glad i went the extra mile. thanks again frank. your expertise is GOLD. bob0 -
Glad to help
how about some pics?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements