Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
hey frank
bob young
Member Posts: 2,177
i will try to do that soon. i did take a few shots but am having some big time computer problems & am waiting for technician to straighten system back to normal operation.
0
Comments
-
hey frank & other experts
need advice on IN6 Burnham steam. doing 3 " drop header. what is advantage if any to use two supply risers as opposed to one single riser which is mandated in piping diagram. thanks gents.0 -
The advantage is
that the steam velocity as it leaves the boiler is cut in half. This further reduces the possibility of water getting up the risers.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
thanks, frank. you are the best
0 -
thanks again frank.
job came out primo. so glad i went the extra mile. thanks again frank. your expertise is GOLD. bob0 -
Glad to help
how about some pics?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements