Dimension \"a\" question per a \"drop header\"
Steamhead (in transit)
Member Posts: 6,688
the dimension almost all boiler makers want for the height of the risers to the header is 24-inches above the highest permissible water level. This is to keep water from getting into the header.
Bob, that 24 inches only applies to the risers. Once they've reached this height (and preferably higher if you can manage it), they can drop pretty much to the top of the boiler if needed. This is the way to connect to any low-hanging steam mains you may have.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Bob, that 24 inches only applies to the risers. Once they've reached this height (and preferably higher if you can manage it), they can drop pretty much to the top of the boiler if needed. This is the way to connect to any low-hanging steam mains you may have.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
I'm over here in Chi-Town and here drop headers are never used. My question is about your Dimension "A" with this type of header, I'm assuming it's from the water-line to the bottom of the Drop- header and is 28" still your magic number?0 -
Drop headers skew the "A" dimension, and make it a non-issue really. The idea of the 28 inches is to give gravity time to fight velocity and prevent water from entering the steam main.
A dropped header slows down the steam and prevents water entering the main.
So to answer your question,.. you dont really need to keep the "A" dimension of the risers going into the drop.
- Norm
- http://www.barefootenergy.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
I think I misunderstood the question, and my answer may be confusing.
In an attempt to clarify,...
The "A" Dimension when looking for the "lowest steam carrying pipe" is something you measure at the end of the steam main, and the dropped header would not be included in the measurement.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
Reply with Pic.
Here is a random picture I took off google to help explain my question. I also have a part 2 to the question0 -
Thank you Frank,
that was kinda what I was waiting for.
24" is the minimum straight-up, then the "drop" can really be as much as you want/boiler permitting?
Dave0 -
Yes
I wouldn't get too close to the waterline though.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thank You old friend!
Dave0 -
Never say never....
I've got one in Chi-town and maybe more to come and a bunch west of Chicago!
You probably want some height for the header above the water line, should you need to drain alot of water out of the header in a hurry if the boiler surges....the taller equalizer of a higher header should give you more room for the water to collect as it reenters the boiler. This is probably not much of an issue on a single zone system since the boiler shouldn't surge like from a zone valve opening.
Boilerpro
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
BLUE TO BLUE
from water line to invert of riser elbow . then as frank said drop it down to top of boiler jacket if necessary0 -
You had it right the first time norm
Thats the B dimesion at end of main. F=Don't doubt yourself buddy. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Drop headers have gotten me out of many jams..........
even without the 28"s and the drop header....very low crawl space...and a boiler replacement where all the old piping was covered in asbestos and they weren't paying to touch it....AND.......WE NEEDED THE MONEY!!!!!!!!!!!!Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements