Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
mixing baseboard with radiators
Options
stanley
Member Posts: 1
We recently installed a Buderus watermaker to an existing gas boiler with cast iron radiators. Our job works to perfection. The customer has one baseboard loop in her kitchen that is not working. someone connected the baseboard loop by removing the caps at the end of the 2-pipe reverse return system and sending it throught the baseboard. Also of interest is the fact that someone previously installed 3 separate self piercing bleeders on this BB loop. I am curious why it will not circulat or heat????
0
Comments
-
how long a run?
probabaly too much pressure drop through the BB... cast rads do not have much if any pressure drop. ..that is why they used them on gravty hot water heat. kpc0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements