QUICK HELP NEEDED ON PRESTIGE ALL

tim smith
Member Posts: 2,850
Buddy of mine up north is helping a friend out on his prestige, getting error E03, wiring harness problem to gas valve. Anybody have any ideas, he is ohming out the harness right now but I have not ever had this error on the prestige. Boiler is 5 mos old. Thanks all in advance, Tim
0
Comments
-
Triangle tube?
I think they use the MCBA control if so,
E03 would be internal control failure0 -
It was internal fault of resistor or diode in plug to gas valve.
Plug and cord replaced, comes as one. Fixed. I got a little info from someone I know that this has been a hit and miss issue, not always but more than just one or two. Tim0