Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

QUICK HELP NEEDED ON PRESTIGE ALL

tim smith
tim smith Member Posts: 2,807
Buddy of mine up north is helping a friend out on his prestige, getting error E03, wiring harness problem to gas valve. Anybody have any ideas, he is ohming out the harness right now but I have not ever had this error on the prestige. Boiler is 5 mos old. Thanks all in advance, Tim

Comments

  • Xc8p2dC
    Xc8p2dC Member Posts: 41
    Triangle tube?

    I think they use the MCBA control if so,

    E03 would be internal control failure
  • tim smith
    tim smith Member Posts: 2,807
    It was internal fault of resistor or diode in plug to gas valve.

    Plug and cord replaced, comes as one. Fixed. I got a little info from someone I know that this has been a hit and miss issue, not always but more than just one or two. Tim
This discussion has been closed.