Splitting hydronic coil in ceiling air handler
Any chance these were frozen at anytime?
  • Ron Meints
    Ron Meints Member Posts: 6
    Hydronic coil tube split
    It has been a while since I looked at a fan coil unit, but never saw this. THere is a split in the copper line. This coil is on the third floor of a condominium, and the second coil to do this. Serial numbers are not close so the manufacturing process should not be the problem (I am looking at this). Has anyone notice water hammer causing a problem on a coil like this, the test rating of the coil is 450 psi and the actual rating of the tubing is 2250 psi. there is a pump with a burst rating far less, and a check valve on it with a bursti ratng of 120psi.
    EBEBRATT-Ed Member Posts: 19,276
    Water or Steam???? I am assuming it's water. Why a check valve?? Could you be trapping water between the check valve and a closed control valve causing a hydraulic problem??????
    Ed
  • Marty
    Marty Member Posts: 109
    A/C ?
    Would this coil happen to be anywhere near a dx cooling coil ??
  • Ron Meints
    Yes, there is a DX coil in the AHU
  • Ron Meints
    These froze in spring,
    warmer weather. There is a check valve in the unit. NO expansion tank.
  • Ron Meints
    Pump,
    There is a grundfos pump with this, and a valve. Again, no air purger or expansion tank.