Taco Room Thermostat
Options
George_15
Member Posts: 24
I would like to use a Taco 568-14 thermostat to replace my exisiting Honeywell T87 thermostat. I have a hot water gas boiler but no Taco zone valves. Instead, I have Honeywell relays that control the booster pumps.
The Taco 568-14 room thermostat is designed for control of Taco Zone valves. It is a simple thermostat with a positive snap action switch and a spiral type bi-metal element for sensitive control. It doesnt have a mercury switch like the Honywell does.
Can I use this Taco thermostat in place of the honeywell T87? Thanks!!
The Taco 568-14 room thermostat is designed for control of Taco Zone valves. It is a simple thermostat with a positive snap action switch and a spiral type bi-metal element for sensitive control. It doesnt have a mercury switch like the Honywell does.
Can I use this Taco thermostat in place of the honeywell T87? Thanks!!
0
Comments
-
Taco Room Thermostat
I would like to use a Taco 568-14 thermostat to replace my exisiting Honeywell T87 thermostat. I have a hot water gas boiler but no Taco zone valves. Instead, I have Honeywell relays that control the booster pumps.
The Taco 568-14 room thermostat is designed for control of Taco Zone valves. It is a simple thermostat with a positive snap action switch and a spiral type bi-metal element for sensitive control. It doesnt have a mercury switch like the Honywell does.
Can I use this Taco thermostat in place of the honeywell T87? Thanks!!0 -
This same question came into every technician at Taco as well.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
wonderful... and the answer is...??0 -
Hi George
Here is Mario's correspondence from this morning. Truthfully, I thought he answered you directly, but after reviewing it I noticed he didn't give you a specific yes, or no. The answer is yes, the T87 is equivalent to the Taco 568-20 analog thermostat. Thank you, for using Taco products, and do not hesitate to contact me directly if you have additional questions or concerns.
Hello George, the Taco stat is just a switch like any other thermostat including the mercury switch type. The part number you reference (568-14) is obsolete; the current model would be 568-20. If you need any further assistance, please feel free to contact us anytime.
Regards,
Mario Silva
Technical Services
Taco Inc.
mailto:marsil@taco-hvac.com
Tel: 401-942-8000 x364
Fax: 401-942-2360
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements