The best bang for the buck in condensing boilers?

Bob Bona_4
Member Posts: 2,080
(Andy Morgan, really,) did 24 Laars HT330's last year on a similar project. Each apt had a zone of bb, and the boiler made domestic internally. Seemed to work well.
0
Comments
-
Best bang for the buck in condensing boilers?
I'm looking to bid a big job with several (over 50), hot water, condensing boilers. I'm trying to find a good overall choice. Owner will be looking HARD at price. Is there one out there that doesn't need primary secondary? I figure this should save price of one pump, fittings, and labor. Also I'm looking for domestic water options. Owner wants all seperate utilities for future tenants. Thank You All for any advice, words of wisdom, war stories, etc.0 -
Do not
try to recreate the laws.
Mod/cons need pumps.0 -
Triangle tube's prestige excellence comes to mind as a well priced unit with self contained DHW and suitability for direct connection. Not too many manufactures will give permission to non primary/secondary piping. Just talked to a friend who did some service work on a trinity boiler, apparently among other problems with the system, the existing 007 primary pump was deemed too small, the manufacturer told him to go to a 0011. I cant imagine a doing a residential heating job that "requires" almost 200 watts just to maintain required boiler flow rates! and then need another pump to get the heat out to the system!0 -
Prestige does not need
to be piped primary secondary and it would be hard to find a nicer boiler at any price.0 -
007 is
too small for NYT.
Read the O & I manuals.0 -
Pumps plural?
I have several successful mod-con's running on on a single circulator. Some of my best work is single pump. The more I look at it single zone single pump is the way to go.0 -
Just another giononie sp. HX If these things need to be pumped so heavily than I would not even consider them.0 -
Patrick, the prestige would be a great choice I feel. Yes they
will be a bit more than some but not near the top in $$. The other thing I would tell the owner is maintenance will be a killer on a lot of the other modcon boilers out there x50. He really needs to look at this because any money he saved upfront he will eat up in maint. & repair. The TT solo boiler has been bullet proof for us. The only problem with the Excellence version of the prestige is it's size for a apt bldg. He may be better off with TT60 & a indirect tank but there goes the cost again. Good luck. Tim0 -
What boilers don't have the giononie?
Thanks0 -
Vitodens 100
has a Viessmann made heat exchanger and is priced very well. What size boilers do you need for this project?
Ted0 -
Boiler sizes
Most of the condos are small one bedroom units.....600 sq ft to 1,000 sq ft max.0 -
I agree.
What's the point when there are better options?0 -
bang for buck
Another important question is what type of radiation. Cast iron mod con OK high temp baseboard you may not get efficiency you expect (boiler not in condensing mode) as well if the loads are small then the boiler will short cycle which kills efficiency. Another option is BTU metering for heat and domestic ( assumes home run supply return back to mechanical room) Alternatively, you can meter off big supply return mains. This is quite common in Europe.0 -
If you don't mind
cast alum..Utica / Dunkirk.
No pri / sec, low press drop H.E. (less than 0.5 psi)0 -
Quit telling everyone about Traiangle Tube!!! I'm having a hard enough time with their delivery backlog.0 -
just my opinion
No boiler with a large delta T and the ability to expand like stainless or aluminum should be piped without primary secondary piping.0 -
I'd be looking
at the Bradford White Combi for a project like this Pat. I would think that it would match-up perfectly!
Leo G0 -
Thanks for the feedback all!
Thanks to all the posters! Info is all good. I'm still "mulling" since we have a couple of months to make a decision. I am leaning towards a combi unit. So far I'm mostly impressed with the Triangle Tube Excellence. Have to do some price shopping at the number of boilers we'll need.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 951 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements