Member Posts: 232
the firing rate motor & programmer are OK.
The S12 G/P has a Manual switch on the control cabinet. If the burner goes in hi fire w/ the manual switch @ Maximum, the problem is in the potentiometer circuit.
May be the pot. Or, it may be an improperly set, or defective, lo fire hold device. Normally an aquastat to keep burner in lo fire until boiler has warmed. Or, modulation may be interlocked thru a heat control. Follow the circuits until you find an open R to B.
The S12 G/P has a Manual switch on the control cabinet. If the burner goes in hi fire w/ the manual switch @ Maximum, the problem is in the potentiometer circuit.
May be the pot. Or, it may be an improperly set, or defective, lo fire hold device. Normally an aquastat to keep burner in lo fire until boiler has warmed. Or, modulation may be interlocked thru a heat control. Follow the circuits until you find an open R to B.
0
Comments
-
power burner issue
have a gordon piatt s12 g 50 power burner, two years old and it won't come into high fire. potentiometer perhaps? not too much experience on this particular unit so any and all help and suggestions welcomed. thanks.0 -
Is the firing rate being controlled automatically by a proportional controller or manually by the knob on the control panel?
Does the firing rate motor go through its full range of movement during prepurge? In purge it should go from minimum to max and back to minimum before ignition sequence is initiated.0 -
Could be as simple as a defective pressure or temp control
depending on type of system. I was looking at a low high low burner yesterday and it would not mod into low fire?? Found closure wire in mod valve was disconnected! Well that was dumb, don't know who did that.0 -
Tim
Maybe a better question would be not who did it but why they did it. A lot of times when I run across something like that I try to find out if someone else has worked on it previously and quiz them or maybe the resident maint personnel0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements