primary secondary -- pumping upstream
don_185
don_185 Member Posts: 312
Why would you need a mixing valve other then using it as a safety.
If the control is controlling floor temps what the harm at feeding alittle 180 into the secondary after a call for domestic.
You always want the secondary to be smaller or match the primary pump.If not, you will turn your return tee into a mixing valve.
  • tomg
    tomg Member Posts: 2
    secondary pump suction is downstream of the outlet
    i'm verifying operation of a prim/sec boiler control. seems to work, but the radiant floor heat circulator sucks /downstream/ and discharges back upstream to the primary circuit. seems like a mixing valve is the proper thing to do, but is this a viable alternative? don't see it in dan's book!
    also piped on the primary is an indirect water heater. the boiler is modulating/ 180F setpt for DHW and 100F for floor heating. secondary circulator is smaller than primary -- 1/25 hp vs 1/8 hp i think.
    any thoughts or resources on this? thanks much!
  • tomg
    for temp control
    actually, by pumping backwards they are using the return tee to mix -- the return mixes with primary and then is supplied to the secondary. Seems like with this setup there is no temperature control -- starts out very cool (cold return water) and gets very warm if the dhw calls (which it does frequently -- this is a restaurant).
    does anyone else pump backwards on their secondary?
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,406
    Yes viega mixing stations http://www.viega.net/5144.html cut and paste this link for their page.
    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating